Service 400A

Leonan

Member
Location
Massachusetts
Occupation
Electrician
Hello everyone, I have a question at work. To provide a 400A service for 6 units, I will use only one pipe and leave the wires in parallel. So will I have to apply table 310.25 C1? Which would be 400A/80%: 500A/2: 250A per phase. Would it have to be a 350 kmil aluminum parallel?
 
Are you asking about the derating or ampacity adjustment table? Youve got a misprint that's T310.15(C)(1). If so your calculations are correct.
 
Yes it is the table 310.15 C1
With a 90° C conductor:
350kcmil aluminum is rated at 280 amp @ 90° C.
300 kcmil aluminum is rate at 260 amps @ 90° C.
260*2*80%=416 amps so 300 kcmil would work.
 
Top