Rearic
Member
- Location
- Medina, NY, usa
Guys, I'm in need of some re-education.
I've got a service ( 200 amp) with a 200 amp meter/main combo on the outside. #2/0 cu. service conductors.
Let's say I feed an A/c outside with a 50 a and then come off the bottom of the panel go through the wall to the inside of the garage and feed a 200 amp panel.
1) does the feeder through the wall have to be #4/0 because it is no longer covered by the .83 reduction?
2) does the inside panel need a main?
any thoughts ?
I've got a service ( 200 amp) with a 200 amp meter/main combo on the outside. #2/0 cu. service conductors.
Let's say I feed an A/c outside with a 50 a and then come off the bottom of the panel go through the wall to the inside of the garage and feed a 200 amp panel.
1) does the feeder through the wall have to be #4/0 because it is no longer covered by the .83 reduction?
2) does the inside panel need a main?
any thoughts ?