Re: Service bond
In case you are refering to bonding the interior water pipe as required by Section 250.104, where the water pipe is NOT a grounding electrode, no, you still may not bond to the gas pipe. 250.104(A)(1) lists the items that may be used to provide this bond: the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor (where large enough), or to an existing grounding electrode. Said grounding electrode will have grounding electrode conductors bonding it to the service enclosure and to the grounded conductor at the service. It is very clear the NEC wants interior water piping to be bonded to the grounding electrode system directly. The size is to be based on Table 250.66 (same size as for the GEC)
Section 240.104(B) covers "other metal piping" which includes gas piping. This section specifically permits the EGC to be the bond.
The only time we require gas piping to be bonded is when the building was wired with knob and tube, older AC(no internal bond strip) or older NM without grounds.
Earl