Bill Smith61
New User
- Location
- NY
- Occupation
- Electrician
So I installed an 800 am 3 phase 120/208 service. This utility’s service feedres came into a 3’x3’ CT cabinet spect out by the utility company. Out of the CT cabinet I ran 2 4” EMT conduits and parallel 750 mcm to an 800 amp main breaker. In each of the conduits I ran a #4 copper with bonding bushings on either end of the 4” EMT’s from the MDP to the meter cabinets case. Mind you the electrical inspection passed 100% and I am good to go. So the utility companies metering dept. “Rochester Gas and Electric“ comes to hook up the CT’S and the lineman are waiting to energize the system. The utility companies metering guy tells me that I can’t have the bonding wire with bonding bushings connected because it interferes with his system. After a 12 hour day I am very tired and arguing with this guy and I eventually just took the bonding wires completely out . Any input on this ?