Strathead
- Ocala, Florida, USA
- Electrician/Estimator/Project Manager/Superintendent
OK maybe this has been asked.  I was looking for a Mike Holt picture (I thought I saw once) that covered this installation and I can only find similar so here goes:
And my multipart question.
We are going around and around about this and the code really chases you back and forth. Please try to reference code that clears this up if you can.
			- Overhead service in RMC to the meter enclosure.
- Grounding electrode conductor brought to the meter and bonded to neutral which is in turn factory bonded to the meter enclosure.
- conductors now must leave the meter enclosure and travel to the Service Disconnect.
- Unless this is wrong, the grounded conductor and the service enclosure and hence the "ground bus" must be bonded together in the service enclosure per 250.24 (B) regardless of where the along the service conductors the grounding electrode connection is made.
- Does there need to be a grounding equipment conductor between the meter enclosure and the service enclosure?
- If yes, then why is such a big deal made out of "parallel ground paths" when this one is OK?
- I can see by many MH examples that the parallel paths is OK because he shows metal conduit between the items. So my real question is whether a 3 conductor SE cable or PVC conduit is OK between the meter enclosure and the service enclosure since there is a fault path between them via the grounded conductor bonded at both devices?