Greetings,
I am inspecting a new 400 amp service. The 400 amp service disconnect is attached to the outside of the building. There are two 200 amp panel boards located just inside and connected with non metal raceways. These are main breaker panels. Since the panel boards are down stream and in seperate enclosures from the service disconnect are they treated as main panels or sub-panels. I have been trying to evaluate whether the bonding conductors are sized properly. There are #4 AWG bare copper conductors routed with the feeder conductors and originating at the aluminum lug where the system grounded and GEC are landed in the service disconnect enclosure and landed on the equipment grounding terminals in the panel boards. Are these system bonding jumpers or ?
I am inspecting a new 400 amp service. The 400 amp service disconnect is attached to the outside of the building. There are two 200 amp panel boards located just inside and connected with non metal raceways. These are main breaker panels. Since the panel boards are down stream and in seperate enclosures from the service disconnect are they treated as main panels or sub-panels. I have been trying to evaluate whether the bonding conductors are sized properly. There are #4 AWG bare copper conductors routed with the feeder conductors and originating at the aluminum lug where the system grounded and GEC are landed in the service disconnect enclosure and landed on the equipment grounding terminals in the panel boards. Are these system bonding jumpers or ?