We have a facility nearing completion wired by an outside contractor that we are doing some inspections on. There is a 25kv loop that feeds a xfmr at each bldg, that is 480/277wye secondary. There is a ground rod system for each building that is bonded to the XO of the xfmr. There are five wires run from the service panel to the xfmr, with the neutral and ground split at the service panel. Normally you bond the N/G at the service. In this case, would the 25kv originating switchgear from the utility be considered the service and the lines into the building considered feeders? Should there be another seperate GEC run to the panel, or since the one coming to the panel is connected to the GEC in the xfmr, would it be redundant. The GEC from the ground rods runs straight to the xfmr and terminates in the same place as the Neutral and Grounding conductor that runs to the panel in the building. Also, the secondary that comes into the building panel is unfused, and where they enter into a trough, branch circuit wires join them in the same raceway, I know that is a violation if these are considered service conductors, but are they considered service conductors? Sorry so long, just wanted to get info correct.