E ECC Member Location NY Feb 23, 2006 #1 What do you think Guys metal offset nipple between 200A meter and panel back to back....bondin bushing or not? I say yes whats your veiw.
What do you think Guys metal offset nipple between 200A meter and panel back to back....bondin bushing or not? I say yes whats your veiw.
iwire Moderator Staff member Location Massachusetts Feb 23, 2006 #2 Re: Service Bonding Yes a bonding bushing is required on service raceways
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 23, 2006 #3 Re: Service Bonding also, you might want to read this thread about offset nipples on services: http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=11;t=008417#000000
Re: Service Bonding also, you might want to read this thread about offset nipples on services: http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=11;t=008417#000000
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 23, 2006 #4 Re: Service Bonding I agree with Bob. Bonding is required on only one side of the raceway. If the KO's are not concentric, tangential or eccentric, the nipple could be bonded with a bonding locknut, bonding bushing or bonding wedge.
Re: Service Bonding I agree with Bob. Bonding is required on only one side of the raceway. If the KO's are not concentric, tangential or eccentric, the nipple could be bonded with a bonding locknut, bonding bushing or bonding wedge.
E ECC Member Location NY Feb 24, 2006 #5 Re: Service Bonding I did add the MIGB's to both sides, and bonded with #4 copper. Thanks for your replies.
Re: Service Bonding I did add the MIGB's to both sides, and bonded with #4 copper. Thanks for your replies.