masselectrician
Member
- Location
- Mass
I have a new pad mounted transformer with ten conduits going to a transclosure ( just a big JB with four busses). From there I have twelve conduits going into two new main services, six conduits to one and six to the other. The engineer is calling for each service to hit three new ground rods, plus water pipe and building steel. My question is related to bonding the metal sweeps(the pipes are pvc) that come up into the transclosure. I believe all I have to do is install a bonding jumper from each bushing to the transclosure and then land it on the neutral bus in the transclosure. Am I correct in that this is required per 250.80, as well as 250.142. Thanks for the input.