Here is another overcurrent protection based on article 450 and 240 and service breaker panel
I have a 75kva transformer 480V delta to a 208/120 WYE. On the primary side, it?s connected to a service disconnect 100A with (3) #1 and (1) #8. On the secondary side, it?s connected to a 250A breaker service panel with (4) 250KCMIL + (1) #4 GND.
Based on article 450, I should be ok right?
saw article 450, there are two methods
Article 450:
Method 1: Primary protection only ? set no more than 125% primary current rating, and does not required secondary protection
Method 2: Secondary Protection set no more than 125% provided the primary current protection set less than 250%.
Question 2: Interpret article 450?
Question 3:
I have a 200A breaker panel that I want to up to a 250A. Can I just replaced the main breaker instead of replacing the whole panel?
Thanks