I don't know if I'm still fuzzy from the holidays or if the EE is confusing me on this one...
On the attached one-line (hopefully it shows up), Notes 1 & 2, do I really need to run two separate GECs of different sizes from pipe, steel, rebar each to the primary and secondary disconnects? It seems like 250.30(A)(4)Exc.2 and 250.30(A)(5)Exc.2 allow me to use the GEC of the service as the GEC of the SDS secondary as long as I size it based on the secondary conductors [250.66]. Is this how it's typically done?
On a more minor note, if I run a grounding conductor in the slab over to the water pipe, wouldn't it be more effective bare rather than in conduit as is called for?
Thanks as always.
On the attached one-line (hopefully it shows up), Notes 1 & 2, do I really need to run two separate GECs of different sizes from pipe, steel, rebar each to the primary and secondary disconnects? It seems like 250.30(A)(4)Exc.2 and 250.30(A)(5)Exc.2 allow me to use the GEC of the service as the GEC of the SDS secondary as long as I size it based on the secondary conductors [250.66]. Is this how it's typically done?