I use 220 to caculate service ampacity. In doing so I add any A/C units or Heat at 100%. The question came up about adding the 1.25 factor to the motor load when making this caculation.
The reference used was 220.3B(3). I pointed out that this was for branch circuits as the heading of 220.3 indicates. However example D1b adds the
1.25 factor in the caculations. I do not think it is correct to do so but what are your thoughts.