C chad6544 Member Mar 22, 2004 #1 what is the calculated load in amperes, using the optional method, for a 65,000 sq ft chool with a connected load of 600kva? how do i figure this out
what is the calculated load in amperes, using the optional method, for a 65,000 sq ft chool with a connected load of 600kva? how do i figure this out
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Mar 22, 2004 #2 Re: service calc. Is this a test question? The answer is in Art 220. Its not that hard, you just need to take your time and work through it.
Re: service calc. Is this a test question? The answer is in Art 220. Its not that hard, you just need to take your time and work through it.
electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Mar 22, 2004 #3 Re: service calc. Load is calculated in VA, not amperes. See 220.34 for schools. I would suggest reading all of Article 220.
Re: service calc. Load is calculated in VA, not amperes. See 220.34 for schools. I would suggest reading all of Article 220.
charlie Senior Member Location Indianapolis Mar 23, 2004 #4 Re: service calc. This is a duplicate thread.