For design engineers out there, how do you perform service calculation in early stage of the design? Especially new construction with big square footage such as, 200K+ SF. This is very important calculation because this is necessary for the space planning in early stage.
I can’t really use NEC 220 in SD calcs because 220 is based on the connected loads and they are not available in that early stage.
So when I do the load calcs in SD or/and early DD, I use the historic data from the pervious similar projects or other technical references, such as IEEE, ASHRAE depending on the type of the projects and that gives me the pretty good watt/sf value per each type of building. Of course, I always give myself some extra capacity and accounts for the future capacity as well.
Is this code violation since I did not use the 220 method?
I have run into situations where the contractors adding all the panel schedule loads (from the construction set) and my service size doesn’t meet the NEC 220.
For example, for a typical hospital, our historic data (and IEEE references) shows that the building loads are avg. some where around 8 – 10 watts/sf, most times less than 10. So my service size is some where around 13 – 15 watt/sf depending on the location (heating fuel type) and the chiller efficiency (water vs air) etc. We have actually reviewed the utility used of several hospital loads after completion and their peak loads have been well under the 8 watt/sf, most of times. This is an example of the hospitals but other type of building loads are well below that.
But when you add up the panel schedule loads (connected) at the end of the design (CD), it always comes out to be higher than the first estimated watt/sf load, even after the demand factor allowed in NEC 220. Then the contractors claims the building service is under sized per the NEC 220 and we have to upsize the service. But we know it is already oversized and the utility info can support that.
So far, I have talked to couple of AHJs and they accepted my calculations but this question keeps coming up so I just want to see what you guys are doing out there in case there are some AHJs won't accept my approach.
I know there is some leeway in NEC 517.30(D) for the generator sizing but I don’t think there are any exceptions on the service calculation.
Any thoughts?
I can’t really use NEC 220 in SD calcs because 220 is based on the connected loads and they are not available in that early stage.
So when I do the load calcs in SD or/and early DD, I use the historic data from the pervious similar projects or other technical references, such as IEEE, ASHRAE depending on the type of the projects and that gives me the pretty good watt/sf value per each type of building. Of course, I always give myself some extra capacity and accounts for the future capacity as well.
Is this code violation since I did not use the 220 method?
I have run into situations where the contractors adding all the panel schedule loads (from the construction set) and my service size doesn’t meet the NEC 220.
For example, for a typical hospital, our historic data (and IEEE references) shows that the building loads are avg. some where around 8 – 10 watts/sf, most times less than 10. So my service size is some where around 13 – 15 watt/sf depending on the location (heating fuel type) and the chiller efficiency (water vs air) etc. We have actually reviewed the utility used of several hospital loads after completion and their peak loads have been well under the 8 watt/sf, most of times. This is an example of the hospitals but other type of building loads are well below that.
But when you add up the panel schedule loads (connected) at the end of the design (CD), it always comes out to be higher than the first estimated watt/sf load, even after the demand factor allowed in NEC 220. Then the contractors claims the building service is under sized per the NEC 220 and we have to upsize the service. But we know it is already oversized and the utility info can support that.
So far, I have talked to couple of AHJs and they accepted my calculations but this question keeps coming up so I just want to see what you guys are doing out there in case there are some AHJs won't accept my approach.
I know there is some leeway in NEC 517.30(D) for the generator sizing but I don’t think there are any exceptions on the service calculation.
Any thoughts?