I just did a calculation for a friend who is thinking about installing an electric on demand water heater at 27kw
If you do an optional calculation the service load comes in at 125 amps however the water heater load is 112 amps. Imo, the water heater and car chargers should not be using the demand factors because this is crazy.
The standard calculation calls for 225 amp service. This is a small condo 1200 sq. ft with no heat strips but just a heat pump (2 ton) at 2000 watts (approximate)
What are your opinions..... The car charger, not in this example, is on for many hours but the water heater may only be on for as long as a shower may take. This could still be an issue if you shower in the evening when the car is being charged.
If you do an optional calculation the service load comes in at 125 amps however the water heater load is 112 amps. Imo, the water heater and car chargers should not be using the demand factors because this is crazy.
The standard calculation calls for 225 amp service. This is a small condo 1200 sq. ft with no heat strips but just a heat pump (2 ton) at 2000 watts (approximate)
What are your opinions..... The car charger, not in this example, is on for many hours but the water heater may only be on for as long as a shower may take. This could still be an issue if you shower in the evening when the car is being charged.