I have not had to size a service with these loads in a long time, so please check this over
480 volt service with the following loads ( no specs yet just verbal from the hvac guys
(2) chillers with 150 amp MCA each three phase 480v
Each chiller has (4) evaporater fans rated flc 0f 25 amps @240 single phase ( hope these will be rated for 208 also
Misc 208/120 loads consiiting of some lighting and small 5 gal electric water heater
I plan on using (2) 75 kva 480v/208/120 transformers
I took the 150 amp chiller load times 175% based on 440.22A plus the additional 150 amp chiller, plus the 2 75kva transformers giving me a ending value of 493kva/480*1.732 or 593 amps
Does this look like I am on the right path (again it has been awhile)
Thanks