Article 220.87 requires when calculating feeder or service loads that serve existing loads the existing load be increased by 125%.
Article 215.2 requires that the minimum feeder conductor size shall not be less than 125% of the continuous plus 100% of the non-continuous.
The exception to 215.2 suggested that if the overcurrent device is rated for 100% of it's rating that the minimum feeder conductor size shall not be less than 100% of the continuous plus 100% of the non-continuous.
Question: If the overcurrent device is rated for 100% of it's rating, are you still required to increase the load for the existing loads by 125%?
Article 215.2 requires that the minimum feeder conductor size shall not be less than 125% of the continuous plus 100% of the non-continuous.
The exception to 215.2 suggested that if the overcurrent device is rated for 100% of it's rating that the minimum feeder conductor size shall not be less than 100% of the continuous plus 100% of the non-continuous.
Question: If the overcurrent device is rated for 100% of it's rating, are you still required to increase the load for the existing loads by 125%?