I am having a discussion via email with Mike and I don't want to bother him with this too far so I thought maybe I can get my confusion straightened out here. Btw, this discussion got started over some other issue on one of his images.
230.42(A)(1) & (A)(2) is the issue not the exceptions. A1 seems pretty clear and imo, we would also have to take into consideration de-rating and correction when sizing the conductors.
A2 doesn't mention continuous vs non continuous- it just mentions the load to be served. My thinking is that the load to be served would be continuous at 125% + non continuous load anyway and since correction factor and de- rating must be used anyway what is the difference here
230.42(A)(1) & (A)(2) is the issue not the exceptions. A1 seems pretty clear and imo, we would also have to take into consideration de-rating and correction when sizing the conductors.
A2 doesn't mention continuous vs non continuous- it just mentions the load to be served. My thinking is that the load to be served would be continuous at 125% + non continuous load anyway and since correction factor and de- rating must be used anyway what is the difference here
230.42 Minimum Size and Rating.
(A) General. Service-entrance conductors shall have an
ampacity of not less than the maximum load to be served.
Conductors shall be sized to carry not less than the largest of
230.42(A)(1) or (A)(2). Loads shall be determined in accordance
with Part III, IV, or V of Article 220, as applicable. Ampacity
shall be determined from 310.15. The maximum allowable
current of busways shall be that value for which the busway has
been listed or labeled.
(1) Where the service-entrance conductors supply continuous
loads or any combination of noncontinuous and
continuous loads, the minimum service-entrance conductor
size shall have an allowable ampacity not less than the
sum of the noncontinuous loads plus 125 percent of
continuous loads.
Exception No. 1: Grounded conductors that are not connected to an
overcurrent device shall be permitted to be sized at 100 percent of the
sum of the continuous and noncontinuous load.
Exception No. 2: The sum of the noncontinuous load and the continuous
load if the service-entrance conductors terminate in an overcurrent
device where both the overcurrent device and its assembly are listed for
operation at 100 percent of their rating shall be permitted.
(2) The minimum service-entrance conductor size shall have
an ampacity not less than the maximum load to be served
after the application of any adjustment or correction
factors.