Got to replace about 120ft of SE underground that had fault damage and non functioning. Issue is existing is 250kcmil 3 wire, and someone installed a generator and ATS at meter and never changed the bonding at the main panel. Now I believe there was some allowances made in the 2020, but here we are on the 2017.
So to rerun it would seem I must run 4 conductors from ATS to the main panel and change the bonding of the main panel? Now this panel is an older CH but not real old but has no visible location to add a seperate ground bus, (no mounting holes, preformed allowing "at least 2 threads contact" for mounting) and neutral is perminantly bonded (not isolated from enclosure).
(Issues the Generator installer failed to recognize or didn't care about.) ATS is Generac and is service equipment with bonded N/G.
What would others do to make compliance to 2017.
So to rerun it would seem I must run 4 conductors from ATS to the main panel and change the bonding of the main panel? Now this panel is an older CH but not real old but has no visible location to add a seperate ground bus, (no mounting holes, preformed allowing "at least 2 threads contact" for mounting) and neutral is perminantly bonded (not isolated from enclosure).