Service Conductor Size vs OCPD Size

Status
Not open for further replies.

MyCleveland

Senior Member
Location
Cleveland, Ohio
Installed service, load calc per art 220 = 950amps
Installation has Main = 1200A
Service conductors = 3 sets 750 Al , 3 x 385 = 1155amps

Compliant ?
Does art 240.4 (C) apply to services ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Not compliant with a single main. 230.90 is a good Code reference.
 