I'm working my way through the Electrical Exam Prep (2020 edition). In the review questions for chapter 9 there is a Dwelling Unit Optional Load calculation. The result of the load calculation is 112A. Using the next size up rule, that gives 125A service.
For reference, this is question 9.3 in the exam prep book, but you don't need to know the details to answer this question:
Now, the question asks for what size Aluminum conductors to use. The answer given in the answer key is 1/0. At 125A, according to the Ampacity table I think it should be 2/0. So what am I missing?
A guess: The service is 125A, but the actual load calculation is 112A so we use the actual load calculation rather than the service size in the ampacity tables... thus 1/0 (based on 112A demand) vs 2/0 that would be required for 125A.
But this doesn't make sense to me. The feeder conductors should be sized to the match the overcurrent protection since changes in the demand in the home (another air conditioner perhaps) might change the load.