I have a job where the electrician tapped the main service conductors from the transformer inside of an MDP. The reason for the tap was to go from (3) conductors per phase to (2) because there were only two lugs inside the MDP.
This panel has a 600A main inside of it acting as the main disconnect for the whole building and also has other over-current devices for HVAC equipment. The closest code section that I could find is 312.8 which it seems to meet this criteria but im questioning it because they are service conductors being tapped within this panel.
Any other code sections that visit this more specifically?
(Job Permitted Under NEC 2011)
Picture Attached.
Thanks!
This panel has a 600A main inside of it acting as the main disconnect for the whole building and also has other over-current devices for HVAC equipment. The closest code section that I could find is 312.8 which it seems to meet this criteria but im questioning it because they are service conductors being tapped within this panel.