Service Conductors and Service Entrance Conductors

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For the sake of discussion let's use the overhead definitions. I admit I occasionally use these two terms interchangeably but do we really need to two separate definitions?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It would seem that they are the same conductors in some instances but can be different--It may make sense in terms of code rules where this difference can affect the interpretation.
 
For the sake of discussion let's use the overhead definitions. I admit I occasionally use these two terms interchangeably but do we really need to two separate definitions?
Good question. I am not sure what the purpose of separately defining the two is. The 230.40 are for SEC, but the statement in 230.2 effectively expands 230.40 ex 2 to service conductors as well.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Well, just from reading (2017) Article 230 Parts I through IV, one difference between service conductors and service entrance conductors is that the latter are sized to include a 125% factor for continuous loads (230.42(A)(1)). Whereas service conductors are only sized for the load calculated according to Article 220, which has no reference to any 125% factor for continuous loads. (230.23(A) or 230.31(A)).

So if I understand correctly, for the 2020 NEC (assuming no relevant changes), for a residential service with a calculated load of 200A, of which 100A is continuous, you could have the following arrangement:

Service Drop (conductors sized by utility)
Service Point (point of attachment to the structure)
Overhead Service Conductors (200A ampacity)
Outdoor Meter/Emergency Disconnect (200A)
Service Entrance Conductors (225A ampacity)
Indoor Main Breaker Service Panel (225A)

Cheers, Wayne
 