The following came by IM:
Hello, I am new to the forum. I need help on an electrical design i am doing.
I am providing electrical service to five (5) separate multi-family dwelling buildings with total 52 dwelling units plus a community center. The Power Co. is providing the pad mounted dry type delta-wye transformer inside the apartment complex area. Each Multi-family building will have a meter center with a main service disconnect. The service conductors will connect directly to the secondary of the transformer without OCPD.
Below are the service conductors (using USE-2 or XHHW-2) and main fuse size for each building. The farthest apt. building is at least 160 feet away from the Power Co. transformer
Building #1, 2, 3 (10 apt. units) = 4-#500KCM, 350A main fuse
Builing #4 (8 apt. units) = 4-500KCM, 350A main fuse
Building #5 (14 apt. units) = 2 sets of 250KCM, 450A main fuse
Community Building - 4-500KCM, 250A main fuse
Do I consider the 4th cable of the service conductor as current carrying conductor?
I also calculated demand load for using the 52 dwelling units plus the community center, is this ok?
I appreciate your help in advance. Thank you.
Hello, I am new to the forum. I need help on an electrical design i am doing.
I am providing electrical service to five (5) separate multi-family dwelling buildings with total 52 dwelling units plus a community center. The Power Co. is providing the pad mounted dry type delta-wye transformer inside the apartment complex area. Each Multi-family building will have a meter center with a main service disconnect. The service conductors will connect directly to the secondary of the transformer without OCPD.
Below are the service conductors (using USE-2 or XHHW-2) and main fuse size for each building. The farthest apt. building is at least 160 feet away from the Power Co. transformer
Building #1, 2, 3 (10 apt. units) = 4-#500KCM, 350A main fuse
Builing #4 (8 apt. units) = 4-500KCM, 350A main fuse
Building #5 (14 apt. units) = 2 sets of 250KCM, 450A main fuse
Community Building - 4-500KCM, 250A main fuse
Do I consider the 4th cable of the service conductor as current carrying conductor?
I also calculated demand load for using the 52 dwelling units plus the community center, is this ok?
I appreciate your help in advance. Thank you.