Service conductors passing through dist. panel

Status
Not open for further replies.

patricknola

Electrical contractor/Generac Dealer
Location
new orleans, La, United States
Occupation
Electrical contractor.
Good morning, I'm installing a generac generator at my own house. I'm getting ready to mount the transfer switch and the wire pull would be much easier if I ran the conductors from line side of meter through the existing offset nipple, through the existing 150 amp square d hom panel and to the generac transfer switch. Can the 150 amp panel be used as a raceway? TIA
 
The service conductors can run thru the panel but can not share the same raeway as non-service conductors.
 
Good morning, I'm installing a generac generator at my own house. I'm getting ready to mount the transfer switch and the wire pull would be much easier if I ran the conductors from line side of meter through the existing offset nipple, through the existing 150 amp square d hom panel and to the generac transfer switch. Can the 150 amp panel be used as a raceway? TIA
Did you mean "load" side of meter?
 