hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have service conductors from POCO transformer run underground inside the building utility room that has 4000A service disco.
The demand load at 4000a service disconnect is 3200A.
I have email from POCO representative stating that POCO would bring in from POCO transformer 7 sets of 500kcmil AL conductors to the line side terminal of 4000A service disconnect and terminate the conductors at line side terminal of the service disco.
Now I need to size the main bonding jumper and bonding jumper to enclosure and their size depend on the incoming service conductor.
Questions:
1. Would this make the service point at the 4000A service disconnect or not?
2. Are not the service conductors 7 sets of 500kcmil AL small when compared with demand load of 3200A at the 4000A service disco or NEC would not apply sizing those conductors?
The demand load at 4000a service disconnect is 3200A.
I have email from POCO representative stating that POCO would bring in from POCO transformer 7 sets of 500kcmil AL conductors to the line side terminal of 4000A service disconnect and terminate the conductors at line side terminal of the service disco.
Now I need to size the main bonding jumper and bonding jumper to enclosure and their size depend on the incoming service conductor.
Questions:
1. Would this make the service point at the 4000A service disconnect or not?
2. Are not the service conductors 7 sets of 500kcmil AL small when compared with demand load of 3200A at the 4000A service disco or NEC would not apply sizing those conductors?