Service: The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served.

Assume multiple services are allowed to a given structure per 230.2. Can these separate services all be fed from the same utility transformer? That's how I read Article 100.

Each of these services is then allowed up to six disconnects per 230.71. As I read this, these disconnects must be grouped, but only with the other disconnects for the given service.

So theoretically one could have three services each with six disconnects, and each set of disconnects could be located in a different part of the structure.

My specific example is a large apartment complex with two meter stacks. each meter stack is fed from the same transformer but counts as a separate service. The house loads are a separate service also.

Say the house load uses the six-disconnect rule, no main. The meter stacks are each located in opposite ends of the building and have their own disconnect located at the stack.

Is it OK to not have all the disconnects to the building in one location? I can't find anything in the code that says its not, assuming these disconnects are separate services and that multiple services can come from one utility transformer. I think my logic is OK but maybe am missing something. Thanks.

EDIT: clarified the location of meter stack disconnects.
 
Last edited:
It gets more confusing than that. We are allowed seperate service entrance conductors to each "occupancy" or "group of occupancies" - see 230.40 Exception No. 1. Then 230.71(A) says that the disconnect means for each set of service entrance conductors permited by 230.40 "shall consist of not more than six switches...." So we are allowed to have a set of six switches serving as the disconnecting means for each occupancy and there is no limit to the number of occupancies that are allowed in a "building"; and they can all be fed from the same "service". If you have mutiple services, then you are allowed six switches in each occupancy for each service. If you think about it long enough you will definitely get a headache!
 
It's not uncommon in a large structure to have two services in totally seperate locations, utilizing 230.2(B). I'd say the power company has a say in how many VA they will provide, and when to set more services to accomodate their equipment.
 