I had posted recently about 2 services w/ 2 meters on detached garage. The 1 meter is for the house needing 300 amp conductors. When I did a load calculation, the house uses no more than approx. 135A or 32KW. The house was wired with many circuits, and wants to keep the breaker quantity instead of rewiring to reduce the excess of existing breakers. The homeowner wants a generator for the house. I was originally to use a 300 amp transfer switch at the house. Bring in 350MCM alum. service conductors in, and run 2 and 4 SER to a 200 amp main, and a 100 amp sub panel; tapping the load side of the 300 amp breaker in the transfer switch. I doubt he'd want to buy a generator of that size or load shed the hell out of a smaller unit. The other option is to install a trough there w/ two whips to the panels, and use a smaller transfer switch inside or out; to a smaller panel for essential circuits. I'd rather put the trough in the basement, but the trough size would come past the panels for code.
What to do?
HR...
What to do?