230.70(A)(1) states :
A) Service conductors can enter a structure then exit again ?
or
B) If conductors are not considered 'outside the structure' as defined in 230.6 they need to hit a service disconnect nearest the point of entrance ?
Say you have an existing service point that is inside the structure in a utility meter (CT can in an electrical room or flush mount meter in a garage wall etc), then service conductors travel across (non 230.6 space) aka the 'interior' of the building then exits again (230.6 space) into a service disconnect.
Since the service disconnect is outside is it not required to be nearest the point of entrance?
In this case there could be a unlimited length of unfused conductors inside the building.
Thanks for your thoughts
Do you read this asReadily Accessible Location. The service disconnecting
means shall be installed at a readily accessible location either
outside of a building or structure or inside nearest the point of
entrance of the service conductors.
A) Service conductors can enter a structure then exit again ?
or
B) If conductors are not considered 'outside the structure' as defined in 230.6 they need to hit a service disconnect nearest the point of entrance ?
Say you have an existing service point that is inside the structure in a utility meter (CT can in an electrical room or flush mount meter in a garage wall etc), then service conductors travel across (non 230.6 space) aka the 'interior' of the building then exits again (230.6 space) into a service disconnect.
Since the service disconnect is outside is it not required to be nearest the point of entrance?
In this case there could be a unlimited length of unfused conductors inside the building.
Thanks for your thoughts