ggmclain
Member
- Location
- business location Wildwood Fl.
I have a town goverment building that houses the 911 police dispatch area. Already existing is the 1600amp mdp, 1600 amp manual non fused disconnect, Asco 4 wire non service rated automatic transfer switch all located in the electrical room. the main service feed from the power company enters the building throught the slab and connects to the utility side of the transfer switch. The generator ties to the alternate power lugs of the transfer switch. From the load side of the tranfer switch the wires are tied to the line side of the service disconnect, the load side is a direct bar connection to the MDP. A third party has stated to the town that this wiring is incorrect to code and I was asked to check on it for them. I have not found any code that tells me it is wrong and would like a clearification on this. The third party stated that a disconnect must be between the meter and the transfer switch. This work was done in 1999. Thanks for the help