dasan384
Member
- Location
- Miami, Florida
Hello guys, I need an advise for a problem I have with a 4 story building. The Main Electrical Room is located at the second floor of the building. There is no space in ground floor, so the only option I have is that one. I have a 1200 Amp main disconnect switch on the main electrical room,so my problem is with the location of the main service disconnect, I know that it has to be in a readily accessible location as per [230.70(A)(1)], So I was planing to use a Shunt Trip and a push button close to the main entrance. I am confused because a recent addition to Section 230.70 is permission to use shunt trip devices at the service disconnecting means located within the building but locating the shunt trip remote operating devices on the outside of the building or close top main entrance, so this permits the fire department or other emergency response teams to disconnect power to the building without having to enter the building first. My problem is that these remote devices are not listed for use as service disconnecting means, as required by 230.66, so the service disconnecting means must still be in a readily accessible location [230.70(A)(3)]. As before, this will be outside the structure, or if inside nearest the point of entry of the service conductors. Thanks in advance for any suggestion.