Service Disconnect Neutral Bus Requirements

Status
Not open for further replies.

Sparky718

Member
I have a 1200A existing unmetered main disconnect on the exterior of a building with a gutter can and (3) small services. Owner is building out new units on the far end of the building. We added a 800A ECB directly next to the 1200 and paralleled (3) 3" conduit to a new gutter on the far end. We planned to change the existing 4-barrel lugs to 6-barrel to accommodate the new conductors. However, The existing neutral bus will not accept the new lugs and apparently we cant get a larger replacement. In the past I've used a polaris type tap in disconnects for the neutral. I understand i will have to bond the tap to the encloser. Am I reaching, or will this not pass inspection?
 
IIRC you cant use the enclosure as a neutral conductor. You could run a conductor from the existing neutral bus to a new neutral bar, but you would have to size the jumper to the max unbalanced current. Might be best to mount a new neutral bar big enough for everything. Keep in mind the MBJ and GEC connection must land on the same terminal or bus.
 
IIRC you cant use the enclosure as a neutral conductor. You could run a conductor from the existing neutral bus to a new neutral bar, but you would have to size the jumper to the max unbalanced current. Might be best to mount a new neutral bar big enough for everything. Keep in mind the MBJ and GEC connection must land on the same terminal or bus.

Not trying to use the encloser as a neutral... I cant retrofit another neutral bus. I'm asking if I can use a Polaris type multi tap to join all neutral conductors and bond the encloser to the neutral, as required at the first means of disconnect.
 
You've added a new service disconnect, right? And it didn't come with a provision for bonding the enclosure to the neutral bus? What am I missing?

You can splice as many neutral conductors as you want with the polaris. I'm less sure about the bond.
 
If I am understanding correctly, you could take all of your neutrals and the gec to 1 Polaris type terminal block, but then you would need to run a bonding jumper sized off 250.66 to the enclosure of the service equipment.
 
If I am understanding correctly, you could take all of your neutrals and the gec to 1 Polaris type terminal block, but then you would need to run a bonding jumper sized off 250.66 to the enclosure of the service equipment.

I believe that answers my question. I hope the inspector agrees. Thanks Ethan
 