I have a service disconnect on outside of building but my panel is 100 feet away inside the building. Do I need another disconnect in sight of my subpanel?
No main required. The feeder to the panel has protection where it originates at the service disconnect.Ok. Does their need to be a main circuit breaker in the panel or can it be main lug only
Either, within the same structure. Main breaker panels sometimes cost less, and offer convenience.Ok. Does their need to be a main circuit breaker in the panel or can it be main lug only