The following is commentary from the 2005 NEC handbook which is found directly after the actual code text in 230.79:
"Three-wire services that supply one-family dwellings are required to be installed using wire with the capacity to supply a 100-ampere service for all single-family dwellings.
A conductor ampacity of 60 amperes is permitted for other loads. Smaller sizes are permitted down to 14 AWG copper (12 AWG aluminum) for installations with one circuit. Two-circuit installations must have a rating of at least 30 amperes. Exhibit 230.27 illustrates the conductor sizing requirements of 230.79 for ungrounded service-entrance conductors. A single service disconnecting means is required to have a rating of not less than the load to be carried."
Perhaps I have become confused in the way I am reading the code... I am seeing that 230.79 talks about the "minimum rating of the service disconnecting means". I am not seeing where 230.79 addresses the size of the service CONDUCTORS.
In particular 230.79(c) requires a service disconnect rated for 100 amps for a dwelling. What would stop an electrician from installing a 100 amp rated fused disconnect and installing 70 amp fuses with 6awg copper conductors to feed a dwelling as long as the calculated load was met (of course this would be impracticle due to cost).
"Three-wire services that supply one-family dwellings are required to be installed using wire with the capacity to supply a 100-ampere service for all single-family dwellings.
A conductor ampacity of 60 amperes is permitted for other loads. Smaller sizes are permitted down to 14 AWG copper (12 AWG aluminum) for installations with one circuit. Two-circuit installations must have a rating of at least 30 amperes. Exhibit 230.27 illustrates the conductor sizing requirements of 230.79 for ungrounded service-entrance conductors. A single service disconnecting means is required to have a rating of not less than the load to be carried."
Perhaps I have become confused in the way I am reading the code... I am seeing that 230.79 talks about the "minimum rating of the service disconnecting means". I am not seeing where 230.79 addresses the size of the service CONDUCTORS.
In particular 230.79(c) requires a service disconnect rated for 100 amps for a dwelling. What would stop an electrician from installing a 100 amp rated fused disconnect and installing 70 amp fuses with 6awg copper conductors to feed a dwelling as long as the calculated load was met (of course this would be impracticle due to cost).