I know this is a broad question to ask and may warrant serval questions but in a nutshell does the NEC list specifically that a service disconnect ampacity shall only be loaded to a maximum of 80% of its rating.
Meaning if I have a connected KVA load of 817A , calculated at 100% of non continuous and 125% of continuous loads that pushes me into a 1200A disconnect because 80% of a 1000A is 800A.
Have an engineer stating this as a code violation. I understand if it were a branch circuit but a main service disconnect? Did not get the chance to ask him to cite where in the code this is listed.
A good engineering practice, yes.
NEC code requirement, please provide back up. 2014 code edition
Thanks for looking.
Meaning if I have a connected KVA load of 817A , calculated at 100% of non continuous and 125% of continuous loads that pushes me into a 1200A disconnect because 80% of a 1000A is 800A.
Have an engineer stating this as a code violation. I understand if it were a branch circuit but a main service disconnect? Did not get the chance to ask him to cite where in the code this is listed.
A good engineering practice, yes.
NEC code requirement, please provide back up. 2014 code edition
Thanks for looking.