The panel needs a main OCPD, it can be remote from the panel.
The service disconnect needs to be a breaker or fuses.
No.Right?
230.91 says "The service overcurrent device shall be an integral part of the service disconnecting means or shall be located immediately adjacent thereto." I would not call 10' away "immediately adjacent". I would also say service disconnect outside and service overcurrent device inside is not "immediately adjacent," even if they connected via only a 6" nipple through the wall.What NEC article justifies this?
No.
230.91 says "The service overcurrent device shall be an integral part of the service disconnecting means or shall be located immediately adjacent thereto." I would not call 10' away "immediately adjacent". I would also say service disconnect outside and service overcurrent device inside is not "immediately adjacent," even if they connected via only a 6" nipple through the wall.
Cheers, Wayne
That would work if "whatever you want to call it" fits within one of the types enumerated in 230.82 "Equipment Connected to the Supply Side of the Service Disconnect." 230.82(3) on "meter disconnect switches" is the only possibility that seems plausible to me. That term is not defined in the NEC, so not sure how broadly that term can be construed.This case is commercial, but could be considered the MCB inside as Service Disconnect and outside as whatever you want to call it?
That would work if "whatever you want to call it" fits within one of the types enumerated in 230.82 "Equipment Connected to the Supply Side of the Service Disconnect." 230.82(3) on "meter disconnect switches" is the only possibility that seems plausible to me. That term is not defined in the NEC, so not sure how broadly that term can be construed.
Cheers, Wayne