I have a 1200 ampere 277/480 volt service that has a 1200 ampere main switch ahead of the metering. there are 8 meters with 8-200 ampere disconnects in a meter bank. These disconnects and meters are all located outside. The building contains 8 commercial spaces fed by each 200 ampere feeder. Is the 1200 ampere fused & ground fault protected switch considered to be the service disconnect or are the 200 ampere individual meter & mains considered to be the required service disconnect? If the 1200 ampere main ahead of the meter is considered the required main, can it be the required disconnect for multiple offices? All indoor panels also have a disconnect.
If You look at the 1 line diagram for services Figure 230.1, It shows the required disconnecting means after the Terminal box, meter & or other enclosure, This service is underground. This makes me think that the 1200 fused switch is not the service disconnect because it is ahead of the metering.
If You look at the 1 line diagram for services Figure 230.1, It shows the required disconnecting means after the Terminal box, meter & or other enclosure, This service is underground. This makes me think that the 1200 fused switch is not the service disconnect because it is ahead of the metering.