This was posed to me in a PM:
"I have been awarded a job to build services in an orange grove. The equipment served are two 200 hp motors 3ph 480v with softstart controllers. Each controller has a 400 amp breaker within enclosure. I was thinking, could I install a non-fused disconnect at the power company point of attachment, then take the feeders to the breaker in the controller enclosure?"
I posted it in the Forum as I don't find the answer to be "clear-cut"because of 230.91.
IF the controllers happen to be rated as service equipment, then I can see no problem bringing the service conductors straight to the controllers, or, if POCO or anyone desires a disconnect ahead of the controllers, the NF service rated disconnect could be added.
If the controllers are not listed as service equipment there is no problem with adding a service-rated NF disconnect, however I don't feel it would be considered the property "service equipment" as 230.91 requires OCP integral with or adjacent to the disconnect.
Add to the mix, this being outdoors, there would be no limit on the length of conductors whether we consider them service or feeders.
Any insight ?
"I have been awarded a job to build services in an orange grove. The equipment served are two 200 hp motors 3ph 480v with softstart controllers. Each controller has a 400 amp breaker within enclosure. I was thinking, could I install a non-fused disconnect at the power company point of attachment, then take the feeders to the breaker in the controller enclosure?"
I posted it in the Forum as I don't find the answer to be "clear-cut"because of 230.91.
IF the controllers happen to be rated as service equipment, then I can see no problem bringing the service conductors straight to the controllers, or, if POCO or anyone desires a disconnect ahead of the controllers, the NF service rated disconnect could be added.
If the controllers are not listed as service equipment there is no problem with adding a service-rated NF disconnect, however I don't feel it would be considered the property "service equipment" as 230.91 requires OCP integral with or adjacent to the disconnect.
Add to the mix, this being outdoors, there would be no limit on the length of conductors whether we consider them service or feeders.
Any insight ?