VI. Service Equipment ?Disconnecting Means:
Article 230.70 (A)(1) (1) Readily Accessible Location. The service disconnecting
means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of
entrance of the service conductors.
Then we have:
VII. Service Equipment ?Overcurrent Protection:
230.91 Location
The service overcurrent device shall be an integral part of the
service disconnecting means or shall be located immediately
adjacent thereto.
Somebody separate these two articles and their uses for me. Examples would be helpful.
Are disconnecting means and overcurrent protection not synonymous?
What I'm looking for is where can I put my main disconnect? "Nearest point of entry" has been the rule of thumb, not necessarily "adjacent thereto".