Residential installation with a 200 amp meter base away and not attached to the home. Conduit comes out of the ground and up the side of the building and into an LB, then inside the ceiling joyce for 10 feet then down the wall and into the top of the 200 amp MB panel. Inspector says he requires a disconnect on the outside of the house.
I've always used 230.70A9(1) as the guideline for not requiring an additional disconnect in this case. This is in Idaho with no local state or city additional requirements to the NEC.
I have worked in Washington for years and the WAC rule requires no more than 15' of non-fused wire before a disconnect is required.
Thanks for any comments or clarifications you may have.
Rory
I've always used 230.70A9(1) as the guideline for not requiring an additional disconnect in this case. This is in Idaho with no local state or city additional requirements to the NEC.
I have worked in Washington for years and the WAC rule requires no more than 15' of non-fused wire before a disconnect is required.
Thanks for any comments or clarifications you may have.