Service disconnect

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I found that service disconnect need to be located in readily accessible location 230.70(A)(1).

Service disco can be in readily accessible location but enclosure of service disco may not be readily accessible.

Where is it in code that service disconnect itself enclosure needs to be readily accessible?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
What ??
That must be some strong smoke
The service disconnect (breaker/fusible switch etc) will be in an enclosure.
If the disconnect is readily accessible, it's enclosure sure will be,.
 