A aashish.pant7 Member Location Miami, FL Occupation Electrical Engineer Jan 28, 2021 #1 Is service disconnecting means required to have overcurrent protection in all ungrounded conductors for 480/277V?
Is service disconnecting means required to have overcurrent protection in all ungrounded conductors for 480/277V?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jan 28, 2021 #2 See 230.90(A). "... Such protection shall be provided by an overcurrent device in series with each ungrounded service conductor ..."
See 230.90(A). "... Such protection shall be provided by an overcurrent device in series with each ungrounded service conductor ..."