Good point & I can't remember what POCO did after I approved the install.If the disconnect is upstream of the meter wouldn't it be locked by the POCO? How would the fuses be accessible to the customer?
I think you should post this in grounding & bondingA metal service gutter feeding 2 disconnects with pvc nipples with two sets of service conductors 3/0 from meter. What is the best way to bond the gutter?
thanks will tryI think you should post this in grounding & bonding
Please don't ask the same question in two different threads. Please respond to this question here:A metal service gutter feeding 2 disconnects with pvc nipples with two sets of service conductors 3/0 from meter. What is the best way to bond the gutter?
My bad. The question was asked in this thread & I felt it should go to grounding & bonding & sent him there.Please don't ask the same question in two different threads. Please respond to this question here:
service gutter bonding
A metal service gutter feeding 2 disconnects with pvc nipples with two sets of service conductors 3/0 from meter. What is the best way to bond the gutter?forums.mikeholt.com
No problem, that question is better in its own thread since it's a bit off topic for this one.My bad. The question was asked in this thread & I felt it should go to grounding & bonding & sent him there.
Ron
That's my concern as well. How can the utility disconnect be considered the service disconnect? Let me give the BROAD picture:f the disconnect is upstream of the meter wouldn't it be locked by the POCO? How would the fuses be accessible to the customer?
Look at my previous post just above here, I do not believe it meets any of the requirements of 230.82.What code are you under? 2020 NEC 230.85 is a new section & section 230.82 was new in 2017, I think.
2017 section addresses meter disconnects & the 2020 section emergency disconnects.
A service disconnect has to be readily accessible correct? What if the utility company does indeed lock it out? There are just so many things I see wrong with this install design. Not to count their misplacement of EGC's on this service side install (that they consider feeders apparently).If the disconnect is upstream of the meter wouldn't it be locked by the POCO? How would the fuses be accessible to the customer?
To answer my own question here, a locked enclosure requiring keys can still be considered readily accessible (Definitions). If the utility company possesses the keys, however, is this still readily accessible?A service disconnect has to be readily accessible correct? What if the utility company does indeed lock it out? There are just so many things I see wrong with this install design. Not to count their misplacement of EGC's on this service side install (that they consider feeders apparently).
If the disconnect is upstream of the meter wouldn't it be locked by the POCO? How would the fuses be accessible to the customer?
To answer my own question here, a locked enclosure requiring keys can still be considered readily accessible (Definitions). If the utility company possesses the keys, however, is this still readily accessible?