D Djelite Senior Member Location Ny Occupation Electrician May 2, 2022 #1 On a Seperately derived system(transformer) are the service disconnect on the primary side of the transformer ever fused?
On a Seperately derived system(transformer) are the service disconnect on the primary side of the transformer ever fused?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) May 2, 2022 #2 If you're referring to a disconnect on the primary to de-energize the transformer for maintenance they can be fused or unfused.
If you're referring to a disconnect on the primary to de-energize the transformer for maintenance they can be fused or unfused.
D Djelite Senior Member Location Ny Occupation Electrician May 2, 2022 #3 infinity said: If you're referring to a disconnect on the primary to de-energize the transformer for maintenance they can be fused or unfused.under which conditions would you want it fused as opposed to not fused? Click to expand...
infinity said: If you're referring to a disconnect on the primary to de-energize the transformer for maintenance they can be fused or unfused.under which conditions would you want it fused as opposed to not fused? Click to expand...