I am not sure what you are asking?

The NEC requires a disconnecting means for a service in accordance with Part VI and in addition the service requires overcurrent protection in accordance with Part VII of Article 230.

Chris
 

ynot12

Member
Location
Chicago
service disconnect

I just saw a new 600 amp service installed where they came into the building to a non fused disconnect about 7 feet from the outside wall. Then they ran about 20 feet to a 9 gang meter fitting with 100 amp breakers built in for the panel disconnects. What I'm questioning is the non fused disconnect they used. That needs to be fused, Correct?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
If the 600 amp disconnect is the service disconnecting means then yes it should be fused.

Take a look at 230.91 for the location of the overcurrent device for a service.

Chris
 

resistance

Senior Member
Location
WA
I just saw a new 600 amp service installed where they came into the building to a non fused disconnect about 7 feet from the outside wall. Then they ran about 20 feet to a 9 gang meter fitting with 100 amp breakers built in for the panel disconnects. What I'm questioning is the non fused disconnect they used. That needs to be fused, Correct?
I can't picture this. Can you send a picture?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In years past, it has not been unusual to see the application you describe in this area and the AHJ ruled 230.91 as allowing a non-fuse switch as long as the meter-bank/over-current devices were "immediately adjacent".
However, the low AIC ratings of non-fuse disconnects has prevented that on most installations.
 

cpal

Senior Member
Location
MA
I just saw a new 600 amp service installed where they came into the building to a non fused disconnect about 7 feet from the outside wall. Then they ran about 20 feet to a 9 gang meter fitting with 100 amp breakers built in for the panel disconnects. What I'm questioning is the non fused disconnect they used. That needs to be fused, Correct?

were any of the meters added if the original install only had 6 it may have complied with 230.90 (A) exception # 3.
 