Yes... and any other breaker in the MLO panel is also a service disconnecting means (or a disconnect for equipment permitted to be connected on the line side of service disconnecting means per 230.82).Can you use a main lug panel marked suitable for service equipment as a disconnecting means when u feed a subpanel through a breaker on the main lug service panel?
Most "loadcenter" panels are only suitable for use as service equipment if they have a main breaker installed in them and that main provides overcurrent protection for the bus, it possibly can be a backfed breaker with proper hold down kit though. You need to look at instructions.
I guess you don't have to buy them if you don't like them. Not sure what is all out there these days, many manufacturers have gone to main breakers that are not plug on types, but not all have, and sometimes you run into special circumstances where they ordinarily have a bolt on main but in some instances still have a backfed plug on main for a particular unit. One example I can think of is QO series panels are mostly all bolt on style main breakers or for three phase has a wire "link" between a main and the bus, but they generally use a backfed plug on breaker for a main for 100 amp three phase panels.[/COLOR]I see these panels and I just dont like them,,,100 amp breaker on the bus and no main lugs..
Haven't been around much CH, but do recall they were good at doing that with 100 amp mains, wasn't sure if that was still the common practice.It's more that price for the application dictates which one is bought that I may have to install. Ch are the ones that I like the least and I have no legitimate reason other than ,,wasn't there a better way. The ch panels don't even have lugs so that I could make it a sub panel and get all 12 spaces.
Can you use a main lug panel marked suitable for service equipment as a disconnecting means when u feed a subpanel through a breaker on the main lug service panel?
I had to think a bit about what you said there as well as what was in OP, and finally concluded the OP question possibly is can you feed a "subpanel" from a breaker in a MLO service panel (that of course has no more then breakers serving as disconnecting means)?The first panel is a mlo,, no ocpd and you want to feed a mlo panel from a breaker one the first?