I dont know if my original topic posted so i will try again.
Some AHJ in our area consider the Individual Tennant breakers in a group metering system as as a seperate service and allow as many as needed to feed the load without a main disconnecting means in the Metering Tap Box. I have seen group metering with a lot more than
6 meters and tennant breakers without a Main Disconnecting means in the tap box of the group metering.They consider each individual tennant breaker
a new service. I disagree. In my mind if you have more than 6 Tennant breakers in a group metering system, you should be required to have a Main disconnecting Means in the Tap Box feeding the group metering. I consider the service entrance conductors the Wiring from the utility Xfmr to the Group Metering. Not the wiring from the Tennant Breaker to Load.
Who is correct?
Some AHJ in our area consider the Individual Tennant breakers in a group metering system as as a seperate service and allow as many as needed to feed the load without a main disconnecting means in the Metering Tap Box. I have seen group metering with a lot more than
6 meters and tennant breakers without a Main Disconnecting means in the tap box of the group metering.They consider each individual tennant breaker
a new service. I disagree. In my mind if you have more than 6 Tennant breakers in a group metering system, you should be required to have a Main disconnecting Means in the Tap Box feeding the group metering. I consider the service entrance conductors the Wiring from the utility Xfmr to the Group Metering. Not the wiring from the Tennant Breaker to Load.
Who is correct?