I have a panel that is fed by service entrance conductors, the panel is inside a building. The meter and CT's are mounted directly opposite on the outside of this same wall. Within the panel a circuit for a chiller chiller is connected to the service entrance conductors. They are connected using insulation piercing connectors. These unprotected conductors exit the panel and go outside to the chiller disconnect.
According to 250.64 (D)(3) the grounding electrode conductor for the two service disconnects, one the panel and the other the chiller disconnect, can be connected to each grounded conductor in a common location. Currently they are connected in the panel. The mentioned section specifies "...in a wireway or other accessible enclosure on the supply side of the disconnecting means....".
by supply side is the connection okay to be made in the panel as long as it's prior to being the grounded conductor being connected to the panel? Or does it need to be a separate enclosure ahead of both the panel and the chiller disconnect?
Thanks for any feedback.
According to 250.64 (D)(3) the grounding electrode conductor for the two service disconnects, one the panel and the other the chiller disconnect, can be connected to each grounded conductor in a common location. Currently they are connected in the panel. The mentioned section specifies "...in a wireway or other accessible enclosure on the supply side of the disconnecting means....".
by supply side is the connection okay to be made in the panel as long as it's prior to being the grounded conductor being connected to the panel? Or does it need to be a separate enclosure ahead of both the panel and the chiller disconnect?
Thanks for any feedback.