M mpd Senior Member Feb 18, 2005 #1 would like some opinions on this, single family home, 400 amp service, 2-200 amp main breaker panels installed at different locations, I say disconnects must be grouped, panels are at opposite ends of the house.
would like some opinions on this, single family home, 400 amp service, 2-200 amp main breaker panels installed at different locations, I say disconnects must be grouped, panels are at opposite ends of the house.
B bphgravity Senior Member Location Florida Feb 18, 2005 #2 Re: service disconnects The two must be grouped if they are both service disconnects. See 230.72(A)
A allenwayne Senior Member Feb 18, 2005 #4 Re: service disconnects Usually in a residential application 4/0 AL SER from disconnects to main lug panel.Or under slabbed.
Re: service disconnects Usually in a residential application 4/0 AL SER from disconnects to main lug panel.Or under slabbed.
J jimwalker Senior Member Location TAMPA FLORIDA Feb 18, 2005 #5 Re: service disconnects They need to be grouped
A allenwayne Senior Member Feb 18, 2005 #6 Re: service disconnects 200,400,600, .... does it matter all disconnects have to be grouped together.No more than 6 throws of the hand
Re: service disconnects 200,400,600, .... does it matter all disconnects have to be grouped together.No more than 6 throws of the hand
physis Senior Member Feb 18, 2005 #7 Re: service disconnects I'm wondering if both panels are fed by service conductors or if one is fed by feeders.
Re: service disconnects I'm wondering if both panels are fed by service conductors or if one is fed by feeders.