Service Disconnects

Status
Not open for further replies.
This is in reference to article 230.71. I have a pad mounted transformer that will be feeding 15 trailers ( in a private community )If I have a panel board with a main circuit breaker am I still limited to only 6 disconnects per panel board?
 
Re: Service Disconnects

No, once you have established a service disconnecting means, you can have as many feeder disconnects as you would like. The same holds true for the feeder supplies.
 